Air-conditioning for CAREL-ahu_pco -lennox unit)

Post by ludovic cavalier »

Here is a perl script to get CAREL pCOweb Air-conditioning Unit vars :

Tested with perl v5.8.5 built for i386-linux-thread-multi
Cacti Version 0.8.6j
Get intake_temp intake_hum blowing_temp using snmp vars on pCOweb integrated in lexnox Air-conditioning Unit

Used Mib decription : CAREL-ahu_pco_v18.MIB
usage:
./get_temp_hum_lenox.pl <host> <snmp version> < snmp community> <snmp port> <snmp timeout>


Output intake_temp intake_hum blowing_temp

Installation :
untar all
Put the perl scipt in your <path_cacti>/scripts/
Import cacti Xml template
Attachments
sample
sample
graph_image.png (30.33 KiB) Viewed 16376 times
cacti_graph_template_sonde_thermique_clim_lenoxpcoweb.xml.tar
cacti graph template for pCoweb Air-conditioning
(20 KiB) Downloaded 624 times
get_temp_hum_lenox.tar
perl script for pCoweb Air-conditioning : Get intake_temp intake_hum blowing_temp using snmp vars
(10 KiB) Downloaded 671 times
lcavalier
Posts: 8
Joined: Fri May 12, 2006 5:59 am

An other script to get unit state

Post by lcavalier »

Here is a perl script to get CAREL pCOweb Air-conditioning Unit sates :

Tested with perl v5.8.5 built for i386-linux-thread-multi
Cacti Version 0.8.6j
Get vars that returns 0:ON or 1:OFF
fan: fan is ON, actually neens that unit works
comp: compressor is ON
R1: Resistance N° 1 is ON
R2:0 Resistance N° 2 is ON
desum: desumidificator is ON
hum: humidificator is ON
major: major alarm on the unit
minor: minor alarm on the unit

Combined with previous script, you can see why temp goes up ...
usage:
./get_lenox_state.pl <host> <snmp version> < snmp community> <snmp port> <snmp timeout>

Output fan:1/0 comp:1/0 R1:1/0 R2:1/0 desum:1/0 hum:1/0 major:1/0 minor:1/0

nstallation :
untar all
Put the perl scipt in your <path_cacti>/scripts/
Import cacti Xml template
Attachments
cacti_graph_template_etat_sonde_thermique_clim_lenoxpcoweb.xml.tar
cacti graph template for pCoweb Air-conditioning status
(30 KiB) Downloaded 525 times
get_lenox_state.pl.tar
erl script for pCoweb Air-conditioning : status
(10 KiB) Downloaded 469 times
sample1 : showing that unit is witching from resistance 1 to 2
sample1 : showing that unit is witching from resistance 1 to 2
graph_image.png (22.91 KiB) Viewed 16234 times
sample : showing a major alarm due to compressor default
sample : showing a major alarm due to compressor default
graph_image2.png (24.95 KiB) Viewed 16234 times
User avatar
hemul
Posts: 10
Joined: Mon Nov 20, 2006 7:57 am
Contact:

Carel Web gate

Post by hemul »

Hello ,
I have Carel web gate device and in "Devices" tab in Cacti it show snmp error, snmp command works, but i cacti can't receive standard parameters like SysLocation and Description, but All Carel variables work's
I changed your script with my oid's , but it still not work...
In log file i can see "SNMP: Host did not respond to SNMP" but with snmpget all works fine
How can i Disable snmp Check ... ?
lcavalier
Posts: 8
Joined: Fri May 12, 2006 5:59 am

Re: Carel Web gate

Post by lcavalier »

hemul wrote:Hello ,
I have Carel web gate device and in "Devices" tab in Cacti it show snmp error, snmp command works, but i cacti can't receive standard parameters like SysLocation and Description, but All Carel variables work's
I changed your script with my oid's , but it still not work...
In log file i can see "SNMP: Host did not respond to SNMP" but with snmpget all works fine
How can i Disable snmp Check ... ?
No need to disable device snmp Check. pcoWeb can normaly reply.
cacti does a snmpget to check if the host is alive getting SysLocation,Description, ...

Can you run this command on your cacti host and post the output ?

snmpwalk -c your_community -v 1 your_host

Why have you changed to "your oid's" ? Is there any oid's changes between your pcweb and mine ?

Do you get any graph in cacti ?

Anyway, Thanks for using :wink:
User avatar
hemul
Posts: 10
Joined: Mon Nov 20, 2006 7:57 am
Contact:

Post by hemul »

Hello lcavalier,
I have no pcoWEB device, i have Carel WEb Gate i think is something other one ...
I have no replies to sysName.0 and other Mibv2 commands, but all Carel variables from UC mib file are works ....
What can i do ?
lcavalier
Posts: 8
Joined: Fri May 12, 2006 5:59 am

Post by lcavalier »

What parameters do you have on your webgate menu :
SNMP configuration tab
(The SNMP tab is used to configure the SNMP protocol features)
User avatar
hemul
Posts: 10
Joined: Mon Nov 20, 2006 7:57 am
Contact:

Post by hemul »

lcavalier wrote:What parameters do you have on your webgate menu :
SNMP configuration tab
(The SNMP tab is used to configure the SNMP protocol features)
In SNMP configuration tab i have :
Community, Location, Contact, SysName and IP address for traps
But i can't receive this parameters with snmpget/snmpwalk and other mibBrowsers .....
So, I have same problem with my NMS - HP Open View Network Node Manager, NNM can't see this device as SNMP ...
lcavalier
Posts: 8
Joined: Fri May 12, 2006 5:59 am

Post by lcavalier »

Found those limitations in webgate documentation. Perhaps it may help:
WARNING
The maximum length of each string SNMP is:
Max. length of the system variables in the WebGate
System Variable Max. Length
SysName 39 characters
sysContact, sysLocation 79 characters

Moreover, the string have to be composed only of alphanumeric characters (0...9, A...Z and a...z). No spaces or punctuation marks are allowed.
User avatar
hemul
Posts: 10
Joined: Mon Nov 20, 2006 7:57 am
Contact:

Post by hemul »

Hello lcavalier,
A problem with Carel is in next :
Cacti host.php have check for sysDescr.0 and if SysDesc.0 is null or error result is ERROR...
$snmp_system = cacti_snmp_get($host["hostname"], $host["snmp_community"], ".1.3.6.1.2.1.1.1.0", $host["snmp_
version"], $host["snmp_username"], $host["snmp_password"], $host["snmp_port"], $host["snmp_timeout"], SNMP_WEBUI);
if ($snmp_system == "") {
print "<span style='color: #ff0000; font-weight: bold;'>SNMP error</span>\n";
And my Carel Web gate can't respond to this query, but all other queries like SysName.0 and SysLocation.0 works fine ....
bash-2.05# snmpget -v 1 -c public 10.112.x.x .1.3.6.1.2.1.1.5.0
system.sysName.0 : DISPLAY STRING- (ascii): CondEMRKC
bash-2.05# snmpget -v 1 -c public 10.112.x.x .1.3.6.1.2.1.1.6.0
system.sysLocation.0 : DISPLAY STRING- (ascii): EMRKC
bash-2.05# snmpget -v 1 -c public 10.112.X.X .1.3.6.1.2.1.1.4.0
system.sysContact.0 : DISPLAY STRING- (ascii): Undefined
bash-2.05# snmpget -v 1 -c public 10.112.x.x .1.3.6.1.2.1.1.3.0
snmpget: Agent reported error with variable #1.
.iso.org.dod.internet.mgmt.mib-2.system.sysUpTime.0: SNMP: Variable does not exist or access is denied.
bash-2.05# snmpget -v 1 -c public 10.112.x.x .1.3.6.1.2.1.1.1.0
snmpget: Agent reported error with variable #1.
.iso.org.dod.internet.mgmt.mib-2.system.sysDescr.0: SNMP: Variable does not exist or access is denied.
bash-2.05# snmpget -v 1 -c public 10.112.x.x sysDescr.0
snmpget: Agent reported error with variable #1.
.iso.org.dod.internet.mgmt.mib-2.system.sysDescr.0: SNMP: Variable does not exist or access is denied.
Now, in lib/ping.php file , function ping_snmp check for device status by SysUptime.0
/* poll sysUptime for status */
$retry_count = 0;
while (1) {
if ($retry_count >= $this->retries) {
$this->snmp_status = "down";
$this->snmp_response = "Host did not respond to SNMP";
return false;
}
Now, I leave snmp_community blank and cacti will no check it for snmp status...
[size=92][color=red][b]Unix is user friendly , it's just picky about who it's friends are.[/b][/color][/size]
[url=http://www.sib-t.com/]Sib-T[/url]
lcavalier
Posts: 8
Joined: Fri May 12, 2006 5:59 am

Downed Device Detection

Post by lcavalier »

sorry . Can't find any solution for your problem. May be a clue for host check :
When you create a new host, you have the ability to choose how the "Downed Device Detection"

The method Cacti will use to determine if a host is available for polling.
NOTE: It is recommended that, at a minimum, SNMP always be selected.
none
ping
snmp+ping
snmp

In your case you can choose "ping"

sincerely
User avatar
hemul
Posts: 10
Joined: Mon Nov 20, 2006 7:57 am
Contact:

Post by hemul »

Hello,
A solution is : In CACTI , to delete community name from device and create only scripts non SNMP Pooling for this device ....
Your Script is work, but I changed it .
Thank you for quick response...
[size=92][color=red][b]Unix is user friendly , it's just picky about who it's friends are.[/b][/color][/size]
[url=http://www.sib-t.com/]Sib-T[/url]
mircea
Posts: 1
Joined: Thu Jul 01, 2010 6:04 pm

Post by mircea »

I try to write an Integer in pcoWEB using php and snmpset.
Reading values with snmpget is fine but I have problems to write value in pcoWEB
Here is the code.
$snmp_host = "192.168.1.120";
$snmp_community = "public";
$snmp_object = ".1.3.6.1.4.1.9839.2.1.1.1.0";
$snmp_object_integer = ".1.3.6.1.4.1.9839.2.1.3.3.0";
$output .= "<hr />Temperatures<hr />";
$temperature1 = snmpget($snmp_host, $snmp_community, $snmp_object);
$output .= "Temp 1 = ".$temperature1."<hr />";
$temperature2 = snmpget($snmp_host, $snmp_community, $snmp_object_integer);
$output .= "Temp 2 = ".$temperature2."<hr />";

$set_integer = snmpset($snmp_host, $snmp_community, $snmp_object_integer,"i","40");

Here is the error that I received from server

Warning: snmpset() [function.snmpset]: Error in packet: (noSuchName) There is no such variable name in this MIB. in C:\xampp\......

Warning: snmpset() [function.snmpset]: This name does not exist: in C:\xampp\....

Any clue how to fix this issue?

Thanks
Mircea
varsatoru
Posts: 1
Joined: Mon Aug 02, 2010 1:33 pm

errors

Post by varsatoru »

seems to have some errors .. can you update it lcavalier ?
moxxbiales
Posts: 41
Joined: Thu Jun 04, 2015 11:36 am
Location: France

Re: Air-conditioning for CAREL-ahu_pco -lennox unit)

Post by moxxbiales »

Hi there,
I ungrave this topic to get the OID of the ON / OFF value for the fan.
Does anyone have this ?
I can't find the CAREL-ahu_pco_v18 pCOWeb.mib to get it.
thanks