UPS Smart APC templates
Moderators: Developers, Moderators
UPS Smart APC templates
here the graphs for APC Smart ups...
- Attachments
-
- apc_runtime.png (28.51 KiB) Viewed 67650 times
-
- apc_load.png (21.12 KiB) Viewed 67650 times
-
- apc_frq.png (22.22 KiB) Viewed 67650 times
-
- apc_batt_temp.png (18.15 KiB) Viewed 67650 times
-
- apc_amps.png (18.65 KiB) Viewed 67650 times
Last edited by timi on Fri Aug 12, 2011 3:20 am, edited 2 times in total.
download templates from http://docs.cacti.net/usertemplate:host:ups:apc
Last edited by timi on Fri Dec 02, 2011 3:16 am, edited 3 times in total.
I made my own version of voltage monitoring using the APC ups. We're experiencing quite low voltages during the day as you can see....
- Attachments
-
- The white spaces were me messing around with the script.
- graph_image.png (51.91 KiB) Viewed 123232 times
-
- cacti_ups_voltage_monitor.zip
- The php goes in the scripts/ dir, the xml can be imported
- (4.82 KiB) Downloaded 8410 times
- streaker69
- Cacti Pro User
- Posts: 712
- Joined: Mon Mar 27, 2006 10:35 am
- Location: Psychic Amish Network Administrator
streaker69,streaker69 wrote:I've also done some APC Stuff.
http://forums.cacti.net/viewtopic.php?t ... highlight=
This is for Windows. I used apcupsd for Linux, but what I have to do to monitor my APC with Cacti...
Thanks,
Vinicius
-
- Posts: 6
- Joined: Tue May 08, 2007 1:49 am
Sorry but can you explain step by step what i have to do to get such great stuff...
I did in apcupsd.conf
DEVICE myhost:161:APC:private
the restart - OK
in .bash_profile
MIBS=+PowerNet-MIB
export MIBS
then relogin and restart snmpd
so when i type
snmptranslate -On PowerNet-MIB::ups
i see
.1.3.6.1.4.1.318.1.1.1
so it seems normal, but when i try to do next:
snmpget -v2c -c private localhost .1.3.6.1.4.1.318.1.1.1
I got such message
PowerNet-MIB::ups = No Such Object available on this agent at this OID
what's wrong???
PS: and believe i digged inet all across...
I did in apcupsd.conf
DEVICE myhost:161:APC:private
the restart - OK
in .bash_profile
MIBS=+PowerNet-MIB
export MIBS
then relogin and restart snmpd
so when i type
snmptranslate -On PowerNet-MIB::ups
i see
.1.3.6.1.4.1.318.1.1.1
so it seems normal, but when i try to do next:
snmpget -v2c -c private localhost .1.3.6.1.4.1.318.1.1.1
I got such message
PowerNet-MIB::ups = No Such Object available on this agent at this OID
what's wrong???
PS: and believe i digged inet all across...
works fine with
Smart-UPS 2200 and Network management Card
and Battery runtime
http://forums.cacti.net/viewtopic.php?p ... ght=#61000
thx a lot !
Smart-UPS 2200 and Network management Card
and Battery runtime
http://forums.cacti.net/viewtopic.php?p ... ght=#61000
thx a lot !
I've imported the templates and .php per your instructions, but the graph remains blank with "nan" information.hommer wrote:I made my own version of voltage monitoring using the APC ups. We're experiencing quite low voltages during the day as you can see....
Debugging the graph returns this:
RRDTool Command:
c:/rrdtool/rrdtool.exe graph - \
--imgformat=PNG \
--start=-86400 \
--end=-300 \
--title="AH2 UPS1 MDF - Line voltages" \
--rigid \
--base=1000 \
--height=120 \
--width=500 \
--alt-autoscale-max \
--lower-limit=200 \
--vertical-label="Vac" \
--slope-mode \
DEF:a="C\:/Inetpub/wwwroot/cacti/rra/ah2_ups1_mdf_max_voltage_1295.rrd":outp_voltage:AVERAGE \
DEF:b="C\:/Inetpub/wwwroot/cacti/rra/ah2_ups1_mdf_max_voltage_1295.rrd":line_voltage:AVERAGE \
DEF:c="C\:/Inetpub/wwwroot/cacti/rra/ah2_ups1_mdf_max_voltage_1295.rrd":max_voltage:AVERAGE \
DEF:d="C\:/Inetpub/wwwroot/cacti/rra/ah2_ups1_mdf_max_voltage_1295.rrd":min_voltage:AVERAGE \
AREA:a#00FF00:"Output voltage" \
GPRINTLAST:" Current\:%8.2lf %s" \
GPRINTAVERAGE:"Average\:%8.2lf %s" \
GPRINTMAX:"Maximum\:%8.2lf %s\n" \
AREA:b#35962B:"Line voltage" \
GPRINTLAST:" Current\:%8.2lf %s" \
GPRINTAVERAGE:"Average\:%8.2lf %s" \
GPRINTMAX:"Maximum\:%8.2lf %s\n" \
LINE1:c#6DC8FE:"Maximum voltage" \
GPRINT:c:LAST:"Current\:%8.2lf %s" \
GPRINT:c:AVERAGE:"Average\:%8.2lf %s" \
GPRINT:c:MAX:"Maximum\:%8.2lf %s\n" \
LINE1:d#FFF200:"Minimum voltage" \
GPRINT:d:LAST:"Current\:%8.2lf %s" \
GPRINT:d:AVERAGE:"Average\:%8.2lf %s" \
GPRINT:d:MIN:"Minimum\:%8.2lf %s\n" \
HRULE:204#FFC73B:"Low transfer voltage" \
HRULE:252#FFC73B:"High transfer voltage"
RRDTool Says:
OK
Debug of Data Source:
Data Source Debug
c:/rrdtool/rrdtool.exe create \
C:/Inetpub/wwwroot/cacti/rra/ah2_ups1_mdf_max_voltage_1295.rrd \
--step 300 \
DS:line_voltage:GAUGE:600:0:260 \
DS:min_voltage:GAUGE:600:0:260 \
DS:outp_voltage:GAUGE:600:0:260 \
DS:max_voltage:GAUGE:600:0:260 \
RRA:AVERAGE:0.5:1:600 \
RRA:AVERAGE:0.5:6:700 \
RRA:AVERAGE:0.5:24:775 \
RRA:AVERAGE:0.5:288:797 \
RRA:MIN:0.5:1:600 \
RRA:MIN:0.5:6:700 \
RRA:MIN:0.5:24:775 \
RRA:MIN:0.5:288:797 \
RRA:MAX:0.5:1:600 \
RRA:MAX:0.5:6:700 \
RRA:MAX:0.5:24:775 \
RRA:MAX:0.5:288:797 \
RRA:LAST:0.5:1:600 \
RRA:LAST:0.5:6:700 \
RRA:LAST:0.5:24:775 \
RRA:LAST:0.5:288:797 \
What am I doing wrong? Thanks...
UPDATE:
OK, I built my own from scratch using the HowTo tutorials. I created an Aggregate 4 of Input Voltage, Output Load %, Temperature and Battery Remaining. The only weirdness I'm getting now is that the Temperature is being reported as 288k (!) which of course is causing that to be at the top and everything else hugging the X-axis.
I'm using OID .1.3.6.1.4.1.318.1.1.1.2.2.2.0. When I do an SNMPWALK of that OID, I get this:
c:\>snmpwalk -c community -v 1 10.1.1.2 .1.3.6.1.4.1.318.1.1.1.2.2.2.0
SNMPv2-SMI::enterprises.318.1.1.1.2.2.2.0 = Gauge32: 28
... so it looks like perhaps it's getting inflated by 10^3? I've gone over and over the Data Template, but I can't see where this is happening... arg!
OK, I built my own from scratch using the HowTo tutorials. I created an Aggregate 4 of Input Voltage, Output Load %, Temperature and Battery Remaining. The only weirdness I'm getting now is that the Temperature is being reported as 288k (!) which of course is causing that to be at the top and everything else hugging the X-axis.
I'm using OID .1.3.6.1.4.1.318.1.1.1.2.2.2.0. When I do an SNMPWALK of that OID, I get this:
c:\>snmpwalk -c community -v 1 10.1.1.2 .1.3.6.1.4.1.318.1.1.1.2.2.2.0
SNMPv2-SMI::enterprises.318.1.1.1.2.2.2.0 = Gauge32: 28
... so it looks like perhaps it's getting inflated by 10^3? I've gone over and over the Data Template, but I can't see where this is happening... arg!
-
- Posts: 6
- Joined: Fri Jul 25, 2008 1:19 am
Hello.
First of all I want to thank everyone that contributed to cacti, it's an awesome program.
I'm quite new to cacti so I'm sorry if I'm asking noobish questions.
I downloaded the templates, however I couldnt find any quide on how to install them and get them working, did I download the wrong file?
I imported the templates into Cacti, but what do I do after that?
I've tried making a hosttemplate that uses the graph- and datatemplate but without luck so far.
Where can I find instructions on how to install the tempaltes to get them working?
I'm runnning the latest (0.4) of CactiEZ.
Thanks in advance,
General_Dark
First of all I want to thank everyone that contributed to cacti, it's an awesome program.
I'm quite new to cacti so I'm sorry if I'm asking noobish questions.
I downloaded the templates, however I couldnt find any quide on how to install them and get them working, did I download the wrong file?
I imported the templates into Cacti, but what do I do after that?
I've tried making a hosttemplate that uses the graph- and datatemplate but without luck so far.
Where can I find instructions on how to install the tempaltes to get them working?
I'm runnning the latest (0.4) of CactiEZ.
Thanks in advance,
General_Dark
Graphs are working, but not retaining data
So, I've got these APC graphs (the original ones up top) setup and working, but they are not retaining data. Every day when I check them, the graphs only show data for the last 12 hours.
Any ideas why the rra's aren't retaining the data?
Any ideas why the rra's aren't retaining the data?
-
- Posts: 1
- Joined: Fri Feb 12, 2010 2:13 am
APC UPS monitoring
If your cacti server is on Linux, you can use the following graph templates:
1. APC battery capacity
2. APC output load
3. APC runtime remaining (in minutes)
4. APC inline voltage and ups output voltage (in VAC)
1,2,4 use SNMP get for data input
3 gets data from a shell script due to the fact that runtime is in timeticks (not gauge) so require a little conversion to minutes, otherwise it's also getting the input data through snmpget.
For those who wants to do your own work from scratch, hope the following OIDs will be useful to you (they should be universal across _all_ APC USP):
.1.3.6.1.4.1.318.1.1.1.2.2.1.0 upsAdvBatteryCapacity (gauge, in %)
.1.3.6.1.4.1.318.1.1.1.4.2.3.0 upsAdvOutputLoad (gauge, in %)
.1.3.6.1.4.1.318.1.1.1.4.2.1.0 upsAdvOutputVoltage (gauge, in VAC)
.1.3.6.1.4.1.318.1.1.1.4.2.2.0 upsAdvOutputFrequency (gauge, in Hz)
.1.3.6.1.4.1.318.1.1.1.3.2.1.0 upsAdvInputLineVoltage (gauge, in VAC)
.1.3.6.1.4.1.318.1.1.1.3.2.4.0 upsAdvInputFrequency (gauge, in Hz)
.1.3.6.1.4.1.318.1.1.1.2.2.3.0 upsAdvBatteryRunTimeRemaining (timeticks)
Output unit of these OIDs depends on how you configure your UPS (ie. if your UPS is configure to display temperature in Celcius, the the output value will be in Celcius). These are coming from APC9616 Network Management Card EM. Your mileage may vary.
.1.3.6.1.4.1.318.1.1.10.1.3.3.1.4.0 emStatusProbeCurrentTemp (gauge)
.1.3.6.1.4.1.318.1.1.10.1.3.3.1.6.0 emStatusProbeCurrentHumid (guage)
1. APC battery capacity
2. APC output load
3. APC runtime remaining (in minutes)
4. APC inline voltage and ups output voltage (in VAC)
1,2,4 use SNMP get for data input
3 gets data from a shell script due to the fact that runtime is in timeticks (not gauge) so require a little conversion to minutes, otherwise it's also getting the input data through snmpget.
For those who wants to do your own work from scratch, hope the following OIDs will be useful to you (they should be universal across _all_ APC USP):
.1.3.6.1.4.1.318.1.1.1.2.2.1.0 upsAdvBatteryCapacity (gauge, in %)
.1.3.6.1.4.1.318.1.1.1.4.2.3.0 upsAdvOutputLoad (gauge, in %)
.1.3.6.1.4.1.318.1.1.1.4.2.1.0 upsAdvOutputVoltage (gauge, in VAC)
.1.3.6.1.4.1.318.1.1.1.4.2.2.0 upsAdvOutputFrequency (gauge, in Hz)
.1.3.6.1.4.1.318.1.1.1.3.2.1.0 upsAdvInputLineVoltage (gauge, in VAC)
.1.3.6.1.4.1.318.1.1.1.3.2.4.0 upsAdvInputFrequency (gauge, in Hz)
.1.3.6.1.4.1.318.1.1.1.2.2.3.0 upsAdvBatteryRunTimeRemaining (timeticks)
Output unit of these OIDs depends on how you configure your UPS (ie. if your UPS is configure to display temperature in Celcius, the the output value will be in Celcius). These are coming from APC9616 Network Management Card EM. Your mileage may vary.
.1.3.6.1.4.1.318.1.1.10.1.3.3.1.4.0 emStatusProbeCurrentTemp (gauge)
.1.3.6.1.4.1.318.1.1.10.1.3.3.1.6.0 emStatusProbeCurrentHumid (guage)
- Attachments
-
- cacti_apc_ups.tar.gz
- APC battery capacity, output load, runtime remaining, and inline/output voltage monitoring.
- (5.06 KiB) Downloaded 4870 times
Who is online
Users browsing this forum: No registered users and 0 guests