UPDATED: APC Graphs plus Amperage used Calculation
Moderators: Developers, Moderators
UPDATED: APC Graphs plus Amperage used Calculation
Hello.
I have attached some screen shots of the APC templates I have made. I am willing to share but not sure of if people will be interested since what I have to offer is already mostly available. Please review and let me know what you think. The only thing I can think of that I have left out is humidity on the temperature graph (I am using an AP9619 w/ Temp probe and not Temp+Humidity).
UPDATE 2009-07-28:
I've made a graph/cdef to estimate your AMP usage for people who need to know relatively how much power they are using in their rack. How I get this value is take the load value divide by the VA rating then divide by the input voltage.
The only problem with this is that in the CDEF I could not think of a way to dynamically get the VA rating of the UPS since its not listed in the Powetnet MIB. Therefore I manually added it into the CDEF.
CDEF: cdef=a,3,*,10,*,e,/
The 3 in the CDEF represents the VA rating on the UPS in thousands (i.e. 3 means this is an 3000VA ups).
I have attached some screen shots of the APC templates I have made. I am willing to share but not sure of if people will be interested since what I have to offer is already mostly available. Please review and let me know what you think. The only thing I can think of that I have left out is humidity on the temperature graph (I am using an AP9619 w/ Temp probe and not Temp+Humidity).
UPDATE 2009-07-28:
I've made a graph/cdef to estimate your AMP usage for people who need to know relatively how much power they are using in their rack. How I get this value is take the load value divide by the VA rating then divide by the input voltage.
The only problem with this is that in the CDEF I could not think of a way to dynamically get the VA rating of the UPS since its not listed in the Powetnet MIB. Therefore I manually added it into the CDEF.
CDEF: cdef=a,3,*,10,*,e,/
The 3 in the CDEF represents the VA rating on the UPS in thousands (i.e. 3 means this is an 3000VA ups).
- Attachments
-
- APC_graphs.zip
- All graphs listed.
- (206.89 KiB) Downloaded 261 times
-
- How many estimated AMPs your UPS is using
- amp.png (22.39 KiB) Viewed 6921 times
-
- Input/Output Voltage and Input/Output Frequency
- Picture 32.png (21.05 KiB) Viewed 11356 times
-
- Battery charge %, Battery Status, Run time in Minutes, and Load %
- Picture 33.png (24.66 KiB) Viewed 11356 times
-
- Temp probe and battery temperature (using cdef to convert deg. c to f. The 32 figure is due to the UPS not responding and the CDEF adding 32 for the temp conversion. Unsure how to get around this since only the temp probe has the option of using deg. f i
- Picture 34.png (19.75 KiB) Viewed 11356 times
Last edited by rhettardo on Mon Aug 03, 2009 12:15 pm, edited 4 times in total.
- streaker69
- Cacti Pro User
- Posts: 712
- Joined: Mon Mar 27, 2006 10:35 am
- Location: Psychic Amish Network Administrator
Here's the way the temp conversion CDEF's should be. Don't know why your graphs 'wouldn't respond' to them.
- Attachments
-
- SP32-20080805-201644.gif (9.63 KiB) Viewed 11349 times
-
- SP32-20080805-201627.gif (9.39 KiB) Viewed 11350 times
[b]Cacti Version[/b] - 0.8.7d
[b]Plugin Architecture[/b] - 2.4
[b]Poller Type[/b] - Cactid v
[b]Server Info[/b] - Linux 2.6.18-128.1.6.el5
[b]Web Server[/b] - Apache/2.2.3 (CentOS)
[b]PHP[/b] - 5.2.9
[b]MySQL[/b] - 5.0.45-log
[b]RRDTool[/b] - 1.3.0
[b]SNMP[/b] - 5.3.2.2
[b]Plugins[/b]PHP Network Managing v0.6.1, Global Plugin Settings v0.6,thold v0.4.1,XMLPort v0.3.5,CactiCam v0.1.5,NetTools v0.1.5,pollperf v0.32,RRD Cleaner v1.1,sqlqueries v0.2,superlinks v0.8,syslog v0.5.2,update v0.4,discovery v0.9,zond v0.34a,hostinfo v0.2,Bloom v0.6.5,mactrack v1.1,weathermap v0.96a,mobile v0.1
[b]Plugin Architecture[/b] - 2.4
[b]Poller Type[/b] - Cactid v
[b]Server Info[/b] - Linux 2.6.18-128.1.6.el5
[b]Web Server[/b] - Apache/2.2.3 (CentOS)
[b]PHP[/b] - 5.2.9
[b]MySQL[/b] - 5.0.45-log
[b]RRDTool[/b] - 1.3.0
[b]SNMP[/b] - 5.3.2.2
[b]Plugins[/b]PHP Network Managing v0.6.1, Global Plugin Settings v0.6,thold v0.4.1,XMLPort v0.3.5,CactiCam v0.1.5,NetTools v0.1.5,pollperf v0.32,RRD Cleaner v1.1,sqlqueries v0.2,superlinks v0.8,syslog v0.5.2,update v0.4,discovery v0.9,zond v0.34a,hostinfo v0.2,Bloom v0.6.5,mactrack v1.1,weathermap v0.96a,mobile v0.1
I would be very interested in the templates. The ones that I currently use, lack some of the info yours have, such as the remaining runtime... which I have wanted for a long time, and haven't been able to find ones that could run on a windows box... I'm hoping these will If you could link them up, that would be great! Thank you.
Jacob Bergman
Pullman School District
jbergman@psd267.wednet.edu
Operating System: winserv 2003
Webserver: IIS 6.0
Cacti: BETA windows installer 1.5 (BSOD2600)
Pullman School District
jbergman@psd267.wednet.edu
Operating System: winserv 2003
Webserver: IIS 6.0
Cacti: BETA windows installer 1.5 (BSOD2600)
I would be very interested in the templates. The ones that I currently use, lack some of the info yours have, such as the remaining runtime... which I have wanted for a long time, and haven't been able to find ones that could run on a windows box... I'm hoping these will If you could link them up, that would be great! Thank you.
Jacob Bergman
Pullman School District
jbergman@psd267.wednet.edu
Operating System: winserv 2003
Webserver: IIS 6.0
Cacti: BETA windows installer 1.5 (BSOD2600)
Pullman School District
jbergman@psd267.wednet.edu
Operating System: winserv 2003
Webserver: IIS 6.0
Cacti: BETA windows installer 1.5 (BSOD2600)
All,
Here is the host template. The only thing missing is a field for humidity since I personally dont have the humidity sensor. I can easily add this though.
Here is the host template. The only thing missing is a field for humidity since I personally dont have the humidity sensor. I can easily add this though.
- Attachments
-
- cacti_host_template_apc_ups.xml
- APC UPS Host template
- (78.64 KiB) Downloaded 592 times
Ok great thanks !!!
I imported the xml file then I added a device with the Host Template "APC UPS". I can add the 3 graphs but there's no Associated Data Queries : "No associated data queries", so of course the graph will be empty :-/
Do you have any idea of the problem ? Thanks you again!! Nice work !
I imported the xml file then I added a device with the Host Template "APC UPS". I can add the 3 graphs but there's no Associated Data Queries : "No associated data queries", so of course the graph will be empty :-/
Do you have any idea of the problem ? Thanks you again!! Nice work !
Ok I have 2 graphs that seems to work. Can I change the temp in Celcius ? :=)
The graph APC Statistics is not working actually. In debug mode I have :
The graph APC Statistics is not working actually. In debug mode I have :
Code: Select all
RRDTool Command:
/usr/bin/rrdtool graph - \
--imgformat=PNG \
--start=-86400 \
--end=-300 \
--title="ups - APC Statistics" \
--base=1000 \
--height=150 \
--width=600 \
--alt-autoscale-max \
--lower-limit=0 \
--vertical-label="" \
--slope-mode \
--font TITLE:10: \
--font AXIS:6: \
--font LEGEND:8: \
--font UNIT:6: \
DEF:a="/var/www/html/website/protected/cacti/rra/ups_apc_charge_53.rrd":apc_charge:AVERAGE \
DEF:b="/var/www/html/website/protected/cacti/rra/ups_apc_charge_53.rrd":apc_charge:MAX \
DEF:c="/var/www/html/website/protected/cacti/rra/ups_apc_runtime_56.rrd":apc_runtime:AVERAGE \
DEF:d="/var/www/html/website/protected/cacti/rra/ups_apc_runtime_56.rrd":apc_runtime:MAX \
DEF:e="/var/www/html/website/protected/cacti/rra/ups_apc_load_55.rrd":apc_load:AVERAGE \
DEF:f="/var/www/html/website/protected/cacti/rra/ups_apc_load_55.rrd":apc_load:MAX \
DEF:g="/var/www/html/website/protected/cacti/rra/ups_apc_batt_status_54.rrd":apc_batt_status:LAST \
DEF:h="/var/www/html/website/protected/cacti/rra/ups_apc_batt_status_54.rrd":apc_batt_status:MAX \
CDEF:cdefg=c,6000,/ \
LINE1:a#2175D9FF:"" \
AREA:a#00A0C1FF:"Charge Percent" \
GPRINT:a:LAST:"Current%8.2lf %s" \
GPRINT:a:MIN:"Min%8.2lf %s" \
GPRINT:a:AVERAGE:"Average%8.2lf %s" \
GPRINT:b:MAX:"Max%8.2lf %s\n" \
LINE1:cdefg#FF5700FF:"" \
AREA:cdefg#EA8F00FF:"Runtime" \
GPRINT:cdefg:LAST:" Current%8.2lf %s" \
GPRINT:cdefg:MIN:"Min%8.2lf %s" \
GPRINT:cdefg:AVERAGE:"Average%8.2lf %s" \
GPRINT:d:MAX:"Max%8.2lf %s\n" \
LINE1:e#FF3932FF:"" \
AREA:e#FF410599:"Load" \
GPRINT:e:LAST:" Current%8.2lf %s" \
GPRINT:e:MIN:"Min%8.2lf %s" \
GPRINT:e:AVERAGE:"Average%8.2lf %s" \
GPRINT:f:MAX:"Max%8.2lf %s\n" \
LINE1:g#FAFD9EFF:"Battery Status" \
GPRINT:g:LAST:"Current%8.2lf %s" \
GPRINT:h:MIN:"Min%8.2lf %s" \
GPRINT:h:MAX:"Max%8.2lf %s\n" \
COMMENT:"-\n" \
COMMENT:"Battery Status 1 = Good, 2 = Change"
RRDTool Says:
ERROR: the RRD does not contain an RRA matching the chosen CF
Here are the C versions. The only difference between these and the previous posted are the lack of a CDEF for converting C to F in the temp graph.
- Attachments
-
- cacti_host_template_apc_ups_c.xml
- apc graph template using C for temp.
- (77.17 KiB) Downloaded 721 times
Template is not loading
Hello,
maybe I'm doing something wrong but I tried to import your templates into cacti version 0.8.6[jk] and 0.8.7a and it always gives me a HASH error. With what version of Cacti did you export the Templates?
maybe I'm doing something wrong but I tried to import your templates into cacti version 0.8.6[jk] and 0.8.7a and it always gives me a HASH error. With what version of Cacti did you export the Templates?